Exam CWBSP Topic 1 Question 51 Discussion

Actual exam question for NFPA's CWBSP exam
Question #: 51
Topic #: 1
A restaurant service area has an 18 ft (5.5 m) high T-Bar ceiling throughout. Using quick-response sprinklers in a wet sprinkler system, what is the minimum area and density that should be calculated?

Suggested Answer: D Vote an answer

In a restaurant service area with an 18 ft high T-Bar ceiling and using quick-response sprinklers in a wet system, the minimum area and density that should be calculated is typically 0.15 gpm over 1,080 ft² (6.1 mm
/min over 100.3 m²), considering the ceiling height and occupancy.
References: NFPA 13 includes design criteria for various occupancies and ceiling types, guiding the selection of appropriate design area and density for sprinkler systems.

by Roberta at Jun 25, 2025, 05:43 AM